About those coffee grounds going down the sink drain... - Page 7

Want to talk espresso but not sure which forum? If so, this is the right one.
User avatar
JohnB.
Supporter ♡
Posts: 6582
Joined: 16 years ago

#61: Post by JohnB. »

What size pipe is it? Looks kind of small for a long run like that.
LMWDP 267

User avatar
slybarman
Posts: 1207
Joined: 12 years ago

#62: Post by slybarman replying to JohnB. »

I want to say 2", but wouldn't swear to it on the bible.

Advertisement
User avatar
JohnB.
Supporter ♡
Posts: 6582
Joined: 16 years ago

#63: Post by JohnB. replying to slybarman »

2" is fine as long as you get that dip out of it. Ideally you want to see a 1/4" per foot slope in your drain pipes.
LMWDP 267

nsuster
Posts: 56
Joined: 3 years ago

#64: Post by nsuster replying to JohnB. »

1/4" per foot minimum for < 2.5" diameter pipe. But note you could slope too much and the liquids may outrun the solids and cause clogs like you're seeing in your pipes. But that is controversial and most codes got rid of max. slope.