by JimG on Wed Dec 14, 2011 3:34 pm
I agree completely with Randy's assessment of the problem with overcoming thermal lag. The Gaggia has a relatively low mass boiler and high wattage heaters, though, so I think it is possible you'd see the effects of the heater near the end of the shot.
Generally, to get the fastest response from your PID when a temperature drop is sensed, you will want a high proportional gain and a high derivative gain. To increase derivative gain normally means increasing the "D" or "rA" rate parameter (units usually seconds or minutes).
Increasing proportional gain usually means lowering "Pb" or "band" (units are degrees), or raising "P" if it is a pure gain (unitless). Sorry for making it so complicated, but different manufacturers define the P, I, and D parameters differently.
Integral, or reset, action does not have much effect in this situation.
Jim