PigSnack wrote:I've seen a couple posts where people note increased performance from a machine that is wired for 20A vs. 15A. I don't understand this as the heating elements are the same wattage in both configurations and should draw equal current. Is it a root-mean-square / Volt Amp f(x) thingy <grin>? Isn't the 20A service more about having a circuit in your kitchen with higher capacity?
Edit...removed irrelevant comments...I finally figured out what was being asked....
As a machine draws more and more power from an electrical circuit, it draws higher current through the wire (as the voltage is "technically" fixed at 120V for the entire circuit for example). But, electrical wire has resistance, and any resistance also introduces a voltage drop across that resistance as current flows, and therefore there is voltage drop across the wire in the circuit, which as an end result, reduces the voltage to the machine. End result - the machine that works "idealy" at 120V, may only be getting an actual 114V, and therefore it gets "sluggish" in performance on a 15A circuit. The machine runs "better" on a 20A circuit because 20A circuits have heavier gauge wire, and heavier gauge wire has less resistance, and therefore there is less voltage drop across the wire, and therefore the machine gets more of the 120V (for example).
If you check some of the home roasting threads, many there use very long extensions cords to accomplish something similar (in reverse)...the long cord induces a voltage drop across the cord, and therefore the voltage to the machine is reduced, and it does not get as hot (they can stretch out their roast times). Makes sense?
Hope that helps....